There was a spur on it before but the extra socket was outside of the small room so i removed it, as far as i am aware the lights are on a ring so i would expect the sockets to be the same.
I think it's time you stopped fiddling with electrics.
As for Ericmark's conclusion that a 'spur' is a 'radial' and vice versa - so they must mean the same thing.....I don't think so.
A radial is a 'layout' of a circuit which starts at the CU and runs to 'wherever it ends', with as many 'branches' as you like.
An 'RFC' is a 'layout' of a circuit that begins and ends at the same protective device, (normally in the CU).
A 'spur' is an 'addition' to a 'radial' or 'RFC'.
Three totally different things.
E.G.
1mm addition to a 1.5mm radial - a spur
1.5mm addition to a 1.5mm radial - extension of radial
1.5mm addition to a 2.5mm radial - a spur
1.5mm addition to a 2.5mm ring - a spur
2.5mm addition to a 2.5mm radial - extension of radial
2.5mm addition to a 2.5mm RFC - a spur
2.5mm addition to a 4.0mm radial - a spur
Simple, really
Which means that adding a '2.5mm radial' to a '2.5mm radial ciruit' is NOT 'against the rules', nor is it a 'spur' - you are just extending the circuit.
The only issue is deciding what the circuit actually is that you want to connect to - but if you can't do that, you shouldn't be fiddling with it anyway.
For the OP:
Assuming we're talking 2.5mm T&E
Confirm which protective device isolates the socket that you wish to connect to. (using safe isolation)
Note the rating of the protective device - if it's 15/16A or 20A then you should be ok to connect an additional socket to it.
If it's 30/32A, then the socket is either part of a 'ring final', or it's a 'spur' off a 'ring final'.
In this case, return to your socket, (whilst still isolated), and do 'end to end' continuity tests on all conductors.
If you get continuity, the socket is part of the 'ring' and you can spur off it.
If you don't get continuity, it's a 'spur' and you can't connect another 'spur' to it, unless it has it's own overcurrent protective device,(e.g. 13A FCU)
If you don't know how to do these tests - get an electrician!