Hi.
I've just bought a Mira Sport 10.8kw shower. The house has a RCD protected consumer unit.
I've fitted 10mm cable, about 10 metres in total length, with 2.5 metres chased in a wall.
1. Is this cable size adequate a friend keeps saying I should have put 16mm in?
2. 10800watts divide by 230v equals 46.9 amps. I can only buy a 40 or 50 amp fuse for our CU, which one do i go for?
Any help much appreciated.