10mm earth to consumer unit
2 Nov 2009
Cleveland
Was told by gas inspector I need gas meter earthing.
More investigating has proven house isnt earthed.
I believe need to run 10mm earth between cold pipe, hot pipe, gas pipe to consumer unit (cable not cut - stripped and clamped at each location)
How do you connect 10mm into CU - all earth terminals seem about 4mm in diameter.
Any help?
Gas and cold pipes only, connected where they enter the property.
You don't usually need to connect to the hot water pipe, unless this enters the property from outside (not likely).
If the terminal holes are 4mm across, 10mm wire will fit in there (10mm refers to the cross sectional area, not the diameter)
When you say the house isn't earthed do you mean you don't have an earth at all to the consumer unit, either from an earth electrode burried in the ground or from the electric suppliers head?
If not then you really need to employ the services of an electrician.
No house I have owned has had an earth from the meter/supplier. Just live/neutral tails.
I thought earthing was done through pipework.
I have owned house for 8 years with no problem. Must have been like this for decades before.
Guess have to get electrician. CU is at front of house - pipes at rear. Electrician probably insists on ripping whole house apart.
Yep, best advice is get an electrician in to have a look. An electrician can install an earth electrode and use that for earthing the system or he may get you to contact the electric board to see if it is possible to get an earth from them.
Earthing of the system and Protective Equipotential Bonding of the extraneous pipework are two different things.