Hello,

I was wondering has anybody got any photos of 17th Edition Consumers they have done or seen,

I would like to see how other people do theres.

Thanks.
 
Sponsored Links
Here's a few different styles that I have installed to "the 17th edition"


IMGP3670.jpg



Iphone171.jpg



Iphone063.jpg





 
Sponsored Links
RF Lighting";p="1609991 said:
Here's a few different styles that I have installed to "the 17th edition"


IMGP3670.jpg



I thought that the neutrals for each Neutral should be separate? why is there a small copper link between each neutral bar wont this affect the rcd for not having them separate for each rcd?
 
The board is a standard non-RCD type. Some of the circuits are protected by RCBOs - the neutrals for these circuits connect to the RCBO. The RCBOs flying leads connect to the neutral rail.
 
ah yes sorry i never noticed that, but if that had been the case there was RCD's that little copper links wouldn't be there correct?? it would have to be split?
 
Yes, if the CU had RCCBs covering a number of circuits then the neutral from each RCCB goes to it's own neutral rail for that group of circuits and the links would be removed.
 
RF: hope your EFLI's were within spec for the C type RCBO's... ;)

Lec: did you seal the top of the CU where the tails entered (416.2.2)? ;)
 