Hi. A questions for the forum
I'll be installing a ring in a new extension. (So far I'm taking lots of care with IEE wiring regs. I need to get it right, and anyway my Building Control officer will need to organize my Building Completion Certificate under Part P sections 1.24..1.27).
So here I have a shallow pitch roof (open to the room) with 150mm PU insulation between rafters and another 25mm PU+plasterboard under. Insulation is not yet in.
BS7671/Table 7.3 in on-site guide says that 2.5mm T+E cannot be used at all for thermal reasons in a ring circuit in a ceiling with >100mm insulation. (method 101). It does not seem to me to distinguish whether the cable is beneath, above or inside the insulation. It seems that I just cant do it. I could do it with 4mm cable, or with 2.5mm used as separate (shorter) radial circuits.
I have asked on electrician who claims he's install it anyway as a ring, and put it above the insulation. (It's OK for partP competent person eh?- but the spotlight would be on me). So is Is this strictly allowed? I don't read that from my understanding of the regulations.
I do see elsewhere on this forum that someone suggests a plastic conduit to bring it through the foam from top to bottom where it needs to penetrate, and provide some ventilation, but again this isn't spelled out in IEE regs as acceptable.
So bottom line, if I install 2.5mm ring ABOVE 175mm insulation with occasional runs THROUGH it, would I get pulled up at inspection time?
Or do I really use 4mm? - Is that really what all you competent persons do? - I don't think there is a new roof anywhere which meets insulation regs with less than 100mm these days.
I'll be installing a ring in a new extension. (So far I'm taking lots of care with IEE wiring regs. I need to get it right, and anyway my Building Control officer will need to organize my Building Completion Certificate under Part P sections 1.24..1.27).
So here I have a shallow pitch roof (open to the room) with 150mm PU insulation between rafters and another 25mm PU+plasterboard under. Insulation is not yet in.
BS7671/Table 7.3 in on-site guide says that 2.5mm T+E cannot be used at all for thermal reasons in a ring circuit in a ceiling with >100mm insulation. (method 101). It does not seem to me to distinguish whether the cable is beneath, above or inside the insulation. It seems that I just cant do it. I could do it with 4mm cable, or with 2.5mm used as separate (shorter) radial circuits.
I have asked on electrician who claims he's install it anyway as a ring, and put it above the insulation. (It's OK for partP competent person eh?- but the spotlight would be on me). So is Is this strictly allowed? I don't read that from my understanding of the regulations.
I do see elsewhere on this forum that someone suggests a plastic conduit to bring it through the foam from top to bottom where it needs to penetrate, and provide some ventilation, but again this isn't spelled out in IEE regs as acceptable.
So bottom line, if I install 2.5mm ring ABOVE 175mm insulation with occasional runs THROUGH it, would I get pulled up at inspection time?
Or do I really use 4mm? - Is that really what all you competent persons do? - I don't think there is a new roof anywhere which meets insulation regs with less than 100mm these days.