I am looking to run a 5.8KW hob and 2.8KW oven on a 40amp circuit, over about 6 metres, with the cable in plastic conduit recessed into a concrete floor.
Will voltage drop and the way the cable is covered affect its ability ?
I work it out at 37amp (@ 230V)
does this sound OK?
Kind regards
Dave
Reply:
"given your oven is less than 3kw, install a socket for it, so its protected by a 13 amp fuse. This can be on the cooker circuit, so it also goes off when you turn off the cooker isolator switch above the 'top.
Make it a 32 amp circuit, with at least 6mm cable
Steve"
Will voltage drop and the way the cable is covered affect its ability ?
I work it out at 37amp (@ 230V)
does this sound OK?
Kind regards
Dave
Reply:
"given your oven is less than 3kw, install a socket for it, so its protected by a 13 amp fuse. This can be on the cooker circuit, so it also goes off when you turn off the cooker isolator switch above the 'top.
Make it a 32 amp circuit, with at least 6mm cable
Steve"