2 Google Nest Thermostats for 2 zones connected to Intergas Rapid 32kw

Joined
4 Apr 2008
Messages
229
Reaction score
12
Location
Glasgow
Country
United Kingdom
Hi,

I would like to connect 2 Google Nest Thermostats for 2 zones to an Intergas Rapid 32kw (used as a combi boiler).

Below is the wiring for the Nest as provided by Google:

upload_2021-10-13_17-49-30.png


Page 63 of the Intergas Rapid 32kw manual shows that the Live and Neutral are on pins 2 and 4 of the X2 connector (refer to screenshot below).

Is this just a matter of connecting both Nest Heat Links as per above diagram and connect the Live and Neutral to pins 2 and 4 of the X2 connector on the Intergas boiler?

Is this really as simple as that?

upload_2021-10-13_17-52-32.png
 
Sponsored Links
Your Switch Live goes to Terminal 1 on X2
I added the terminal # of the boiler (in red) on the diagram below, is this what you mean?

upload_2021-10-13_18-27-23.png
 

Attachments

  • upload_2021-10-13_18-25-31.png
    upload_2021-10-13_18-25-31.png
    61.3 KB · Views: 376
Sponsored Links
Brilliant Andrew, thanks a lot!

PS: regarding the pump inside the combi boiler, do terminal 7 & 8 really need to be connected to Live and Neutral?

Sorry for the silly question, but if I do so I assume the pump will be constantly turned on, shall this actually be Switch Live on terminal 7?
 
The boiler's PCB deals with switching the pump, you don't need to connect anything to that
 
I should have added that the jumper wire between terminals 6 and 7 of connector x4 (installed by default) needs to be removed.
 