So based on the feedback Ive decided to do some calculations. I must admit, Ive had 6 houses over the years, and had the heating system either installed from scratch or by qualified plumbers. I must have had 10+ rads added to the systems at various points too..... honestly, I dont think ive ever seen a plumber perform any kind of calculation, and when adding rads on I dont think ive seen them do anything other than feeding off the nearest 22m, down to 15mm all the way to the rad.... Ive defintly not seen a calculator out.....and ive never had any issues. However, as this is being done from scratch, and Im doing it myself (apart from the comissioning) I thought Id plan it out properly;
Its a build seperate to the main house, with its own 30kw boiler. Its 2 rooms, both on the same level.
Room1 will have two radiators, both 5849 BTU rated.
Room 2 will also have 2 radiators also rated 5849 btu.
radiator 1 in room 1 is 3m away from the boiler.
radiator 2 in room 1 is 7 meters from the boiler.
Radiator 1 in room 2 is 10m from the boiler.
radiator 2 in room 2 is 15m from the boiler.
Each radiator is rated at 5849 BTU.
Room 1 Total Heat Load:
2
×
5849
=
11698
BTU
2×5849=11698BTU
Room 2 Total Heat Load:
2
×
5849
=
11698
BTU
2×5849=11698BTU
Total heat load for the system:
11698
BTU
+
11698
BTU
=
23396
BTU
11698BTU+11698BTU=23396BTU
Boiler to Radiator 1 in Room 1 (3m):
I believe 15mm pipe is sufficient since it can handle up to 15000 BTU/h, and the load is 5849 BTU.
Boiler to Radiator 2 in Room 1 (7m):
The total load up to Radiator 2 will be 11698 BTU. So15mm pipe
Boiler to Radiator 1 in Room 2 (10m):
The total load up to Radiator 1 in Room 2 will be 17547 BTU (11698 BTU from Room 1 + 5849 BTU for Radiator 1 in Room 2). So a 22mm pipe here because a 15mm pipe would be too close to max.
Boiler to Radiator 2 in Room 2 (15m):
The total load up to Radiator 2 in Room 2 will be 23396 BTU. So A 22mm pipe.
Detailed Pipe Layout
From Boiler to Junction for Room 1 and Room 2: Use 22mm pipe.
From Junction to Radiator 1 in Room 1: Use 15mm pipe (3m).
From Junction to Radiator 2 in Room 1: Continue with 15mm pipe (total distance 7m).
From Junction to Radiator 1 in Room 2: Use 22mm pipe up to the point before Radiator 1 (10m), then reduce to 15mm pipe to the radiator.
From Radiator 1 in Room 2 to Radiator 2 in Room 2: Continue with 15mm pipe (total distance 15m).
Summary of Pipe Sizes
Boiler to Split Point: 22mm
Split Point to Radiator 1 in Room 1: 15mm (3m)
Split Point to Radiator 2 in Room 1: 15mm (7m)
Split Point to Radiator 1 in Room 2: 22mm (10m), then 15mm to the radiator
Radiator 1 in Room 2 to Radiator 2 in Room 2: 15mm (15m)
Plan
Ive done a little plan as follows
Be interested to here is you guys think this is ok.