Good Evening ,
I have my 2391 Practical exam on Monday and a few concerns that Im hoping you can help me with
Test 1 - Visual inspection find x amount of faults.. im sure I will be OK with this one
Test 2 - 2 x Insulation Resistance tests... we are to do a complete test so am I right in saying it is main switch off but all MCBS switched on ??
The examiner then flicks a switch and puts a fault on the circuit - I guess the logical way to fault find is to knock off an MCB at a time and retest until by process of elimination you find the faulty circuit (however Im told it can be a N-E fault too) is this how you would approach this test ?
Test 3- Earth Fault loop Impedance Im Ok with this part of the test
Then its onto the full test which I aim to tackle in the following steps
1.Safe Isolation
2.Continuity of bonding and protective conductors
3.Polarity
4.Continuity of Ring Final Circuit Conductors
5.IR ( am I right in saying this will be main switch off and all MCB's off as im sure we have to test each circuit individually )
Im confident up to this point but from here I could do with some clarification so please correct me if im wrong but I think this is the order they want
6.Check supply polarity
If all OK is it time to power up at this stage before your phase rotation ?
If so is it then
7.phase rotation
8.ZE
9.PEFC&PSCC
10.ZS
11.RCD
12.Functional Testing
Im confident enough in the tests but would like some clarification on the order so if you have recently taken the 2391 or even if you havent can you confirm what order you would look to do the tests
Cheers
Stephen
I have my 2391 Practical exam on Monday and a few concerns that Im hoping you can help me with
Test 1 - Visual inspection find x amount of faults.. im sure I will be OK with this one
Test 2 - 2 x Insulation Resistance tests... we are to do a complete test so am I right in saying it is main switch off but all MCBS switched on ??
The examiner then flicks a switch and puts a fault on the circuit - I guess the logical way to fault find is to knock off an MCB at a time and retest until by process of elimination you find the faulty circuit (however Im told it can be a N-E fault too) is this how you would approach this test ?
Test 3- Earth Fault loop Impedance Im Ok with this part of the test
Then its onto the full test which I aim to tackle in the following steps
1.Safe Isolation
2.Continuity of bonding and protective conductors
3.Polarity
4.Continuity of Ring Final Circuit Conductors
5.IR ( am I right in saying this will be main switch off and all MCB's off as im sure we have to test each circuit individually )
Im confident up to this point but from here I could do with some clarification so please correct me if im wrong but I think this is the order they want
6.Check supply polarity
If all OK is it time to power up at this stage before your phase rotation ?
If so is it then
7.phase rotation
8.ZE
9.PEFC&PSCC
10.ZS
11.RCD
12.Functional Testing
Im confident enough in the tests but would like some clarification on the order so if you have recently taken the 2391 or even if you havent can you confirm what order you would look to do the tests
Cheers
Stephen