240v Floodlight Problem
17 Apr 2015
Surrey
I have stuck a floodlight at the top of my garden and connected into an exterior IP65 box via SWA.
I have used the following harmonized scheme and double checked both ends are aligned:
brown - live
grey - neutral
black - earth
I guess this is irrelevant given that I checked both ends are wired same.
Its not working!
I have checked the bulb and its fine and the socket is live.
My voltage detector pen lights up on the cable as it exits the box. The I have buried it 18" deep.
My voltage pen does not light on the cable as it enters the light though.
The distance between ends is about 12 meters.
I am getting a Pro in but just wondered if this sounds normal ie. the distance will impact the power?
Yes, I am a complete amateur Will get a pro in but just trying to learn.
cheers
brown - live
grey - neutral
black - earth
Its not working!
cheers
I hope you have put green/yellow sleeving on the black wire and blue sleeving on the grey wire.
No it is not normal, there is a fault.
Voltage detector pens are pretty useless.
Hopefully your pro will sort it.
cheers for the comments.
Yes, to the sleeving.
The bulb is in about as tight as it will go so maybe the light is faulty.
Will wait for the expert.
cheers.
That could be your test pen misleading you
Check the floodlight has not got a built in light sensor that makes it only work when dark
brown - live
grey - neutral
black - earth
Its not working!
Where are you getting the supply from?
And that the armour is earthed and the cable properly glanded at each end.
Before making this live you should have done continuity of the conductors, IR and polarity.
If your voltage pen is picking up a live at supply side an not at load, you either have bad readings from pen, a break in continuity or possibly, the pen was close enough to another live at supply side to detect a voltage and you have not terminate the live conductor correctly or powered up.
Check for insulation trapped in terminal or loose/broken conductor. And after that, you have power.
But I would recommend that you follow the correct procedures, prior to making the circuit live.