Hi,
I'm looking for a fuse (unless someone comes up with a better idea) to power a computer that, in the event of a short circuit fault in the power supply, will blow while not causing the 16A b-curve breaker that feeds the curcuit to also trip. The circuit is already drawing 12 - 16 amps constantly.
In more detail:
At work we rent power and rack space in a few data centres, and have a few dozen 19" racks of computer equipment (1U servers, mostly). Each rack has its own single power feed via a 16A b-curve breaker back at the data centre's power distribution board. We're not in a position to change the breaker because it belongs to the data centre, not us.
Each rack may have 20 - 30 servers in it, each drawing several hundred milliamps during normal operation. Total draw per rack is approx 12 - 16 amps.
On several occasions we've had power supply failures in a single server that has caused a momentary short sufficient to trip the breaker supplying power to the entire rack, causing all of the equipment in the rack to shut down.
Power distribution *within* each rack is down to us. Currently we have some remotely manageable power distribution units - one 13A plug supplies power to a PDU, which has 8 unfused IEC outlets. We have three PDUs per rack and these feed power to most of the equipment.
I was thinking of the possibility of having an IEC lead with an inline fuse holder with maybe a 2A fast blow fuse in it, maybe a 2A variant of this:
http://www.farnell.com/datasheets/10867.pdf
Am I barking up the wrong tree, or would a 2A variant of the above discriminate with a 16A b-curve breaker that's already drawing close to its rated load?
Thanks for reading through this far
Cheers,
Kingsley.
I'm looking for a fuse (unless someone comes up with a better idea) to power a computer that, in the event of a short circuit fault in the power supply, will blow while not causing the 16A b-curve breaker that feeds the curcuit to also trip. The circuit is already drawing 12 - 16 amps constantly.
In more detail:
At work we rent power and rack space in a few data centres, and have a few dozen 19" racks of computer equipment (1U servers, mostly). Each rack has its own single power feed via a 16A b-curve breaker back at the data centre's power distribution board. We're not in a position to change the breaker because it belongs to the data centre, not us.
Each rack may have 20 - 30 servers in it, each drawing several hundred milliamps during normal operation. Total draw per rack is approx 12 - 16 amps.
On several occasions we've had power supply failures in a single server that has caused a momentary short sufficient to trip the breaker supplying power to the entire rack, causing all of the equipment in the rack to shut down.
Power distribution *within* each rack is down to us. Currently we have some remotely manageable power distribution units - one 13A plug supplies power to a PDU, which has 8 unfused IEC outlets. We have three PDUs per rack and these feed power to most of the equipment.
I was thinking of the possibility of having an IEC lead with an inline fuse holder with maybe a 2A fast blow fuse in it, maybe a 2A variant of this:
http://www.farnell.com/datasheets/10867.pdf
Am I barking up the wrong tree, or would a 2A variant of the above discriminate with a 16A b-curve breaker that's already drawing close to its rated load?
Thanks for reading through this far
Cheers,
Kingsley.