3 port problem

Joined
5 Oct 2010
Messages
8
Reaction score
1
Location
Surrey
Country
United Kingdom
hi can anyone help.i've just been to a call where the customer says they are only getting heat to the upstairs rads.i immediately thought a faulty pump but discovered the 3 port had been left in the manually open position.i put it back to normal and made a demand for heating,the lever moved over but not enough to hit the microswitch.as it was late in the evening i just dry wired a new 3 port in.the lever moved and made the microswitch but the pump failed to start and hence no ignition.the strange thing is with the old 3 port if i pushed the lever that bit further to make the microswitch the pump kicked in and the boiler fired.duff 3 port?????any ideas? would be a great help
 
Sponsored Links
Would imagine the original valve needed a new synchron motor so has just been latched open to bypass it, check the wiring on the replacement and check the pump. May just be that the heating doesn't have chance to warm up before the cylinder stat is satisfied.
 
thanks for the advice. i did try a syncron first but still not working. i didnt get 230v on the orange so im suspecting the 3 port i dry wired is faulty.
 
Sponsored Links
2 seperate actuators getting power to the motor making the microswitch and not putting power down the orange?, sounds unlikely.
 
In order to get 230v on the orange wire when valve opens you must have 230v on the grey wire (either from h/w off on clock or cyl stat satisfied)
 