30A fuse not blowing

Joined
24 Nov 2004
Messages
431
Reaction score
5
Country
United Kingdom
An electric shower is pulling 35A.
its circuit is fused with a 30A-rated cartridge fuse.
why isn't the fuse blowing? do I have a faulty fuse?
what fuse should the circuit be protected with?
 
Sponsored Links
Google “current curves”.

The fuse will likely last many hours with that minor over current. In fact, probably indefinitely.

800px-Curve-BS1361.png
 
Sponsored Links
Misuse of a circuit like that can cause damage to the fuse holder and fusebox as the fuse will likely be running fairly hot.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top