I want to repair a damaged cable using a 30A 3 terminal 4x6mm sq MK junction box.
The damaged cable is 6 mm sq protected by a 32A MCB feeding a 5kW double oven.
Is this acceptable or not? I know that the total load current will not exceed 22A in use. But a fault current could exceed 30A (the junction box rating). Not sure about the rules for junction boxes. All help appreciated. Steve.
The damaged cable is 6 mm sq protected by a 32A MCB feeding a 5kW double oven.
Is this acceptable or not? I know that the total load current will not exceed 22A in use. But a fault current could exceed 30A (the junction box rating). Not sure about the rules for junction boxes. All help appreciated. Steve.