If you are happy with the Nest Heatlink being installed in the same location as the old Drayton, then you can try and connect...I was just wondering if I could install 3rd Gen Nest without new wiring?
Ahhh, you didn't mention an external thermostat, but I should have thought to ask!Here is the old thermostat, got a random number 3 cable there.
View attachment 355484
I know the Nest terminals are tight, but we could really do with seeing less copper showing on the wires!How does this look?
Ahhh, you didn't mention an external thermostat, but I should have thought to ask!
It looks like the Blue (oversleeved black) wire to the thermostat comes from Drayton N and the red wire to thermostat L comes from Drayton terminal 3.
If you want to remove the existing thermostat and reutilise those wires for the 12V supply to the Nest, we need to find where that yellow wire goes - I think it joins with another wire in a separate terminal block behind the Drayton - is that correct?
View attachment 355489
I know the Nest terminals are tight, but we could really do with seeing less copper showing on the wires!
Ahhh, you didn't mention an external thermostat, but I should have thought to ask!
It looks like the Blue (oversleeved black) wire to the thermostat comes from Drayton N and the red wire to thermostat L comes from Drayton terminal 3.
If you want to remove the existing thermostat and reutilise those wires for the 12V supply to the Nest, we need to find where that yellow wire goes - I think it joins with another wire in a separate terminal block behind the Drayton - is that correct?
View attachment 355489
I know the Nest terminals are tight, but we could really do with seeing less copper showing on the wires!
I don't know if you can confirm, but this appears to be the thermostat cable...Seems you're right about it being connected via that unit
I don't know if you can confirm, but this is the thermostat cable...
View attachment 355494
Does the red wire connect to terminal 3, and is the blue (over-sleeved black) in the N terminal?
Ok, perfect!It seems you're right. Terminal 3 red cable belongs to the highlighted possible thermostat cable and the blue (black sleeve) is housed in terminal N comes from that cable, too.
Ok, perfect!
This should help tidy up the wiring a bit.
The blue (oversleeved black) from that cable can be removed from N.
The red can be removed from terminal 3.
The yellow in the separate terminal block (from the other cable) can then be connected to terminal 3 of the Heatlink, in place of the red.
Apart from the earth wire, that should leave all the wires from the thermostat cable decommissioned.
It's possibly an opportune moment to test the system before moving on to the thermostat wiring. (With the cables safe and power restored) Try using the manual override button on the Heatlink - hopefully the boiler should fire.Great, that's definitely a lot more tidy!
It's possibly an opportune moment to test the system before moving on to the thermostat wiring. (With the cables safe and power restored) Try using the manual override button on the Heatlink - hopefully the boiler should fire.
...and hopefully you don't really mean N & L, when talking about connecting up the thermostat to T1 and T2 - 230V AC and 12V DC don't like to mix!
Brilliant, well doneI turned the boiler back on front he isolator and did a manual mode check and all was working well
If all the wires from the thermostat cable have been disconnected as suggested earlier, then you have the choice; you could remove the cable and old thermostat backplate completely; or if you were happy with the position of the old stat, you could reuse this cable to power the new Nest thermostat, i.e. use the red wire in that cable to connect terminals T1 and the blue for T2.On second thoughts though you said the cable was now decommissioned and I should just place the cable 3?
Just to say thanks. All up and running. You've been so helpful.Brilliant, well done
If all the wires from the thermostat cable have been disconnected as suggested earlier, then you have the choice; you could remove the cable and old thermostat backplate completely; or if you were happy with the position of the old stat, you could reuse this cable to power the new Nest thermostat, i.e. use the red wire in that cable to connect terminals T1 and the blue for T2.
That's great to hear - glad you got it sorted.Just to say thanks. All up and running. You've been so helpful.