Hi guys, i'm building an outbuilding which is around 45 mtrs from the house. The lighting will involve a few circuits in 2 rooms. In total, light output will be no more than 1,500watts (1.5kw). for power i'll have an amplifier and subwoofer which'll be around 400-500 watts each, a few av items, mini fridge and a couple of 3kw max radiators. My builder is doing the work and i'm then going to get it signed off by a sparky. He's suggesting a 16mm 3core cable. Thats around £200+VAT. I've spoke to a few gents at TLC who say that 6mm is more than sufficient and that 16mm is totally unnecessary unless i've got massive appliances all wired up at one time, which will never be the case.
Can i please have some views on this. Would 6mm or 10 mm suffice? I was thinking 6...
Also, i read that 2 core should do the job since the armour itself can act as earth. Is this true?
Testing times, credit crunch and all i need to avoid unnecessary costs where possible. Please help!!
Can i please have some views on this. Would 6mm or 10 mm suffice? I was thinking 6...
Also, i read that 2 core should do the job since the armour itself can act as earth. Is this true?
Testing times, credit crunch and all i need to avoid unnecessary costs where possible. Please help!!