Hi, for a kitchen radial circuit supplying a total of 5.2kw of fixed load (dishwashers, washer/dryer, hob, etc) plus two 2g sockets, this would normally be fine for 4mm csa on a 32a rcbo, however the circuit passes through 2m of ducting with other circuits so derating brings it below 32a, and using a 20a rcbo could be a solution (allowed on radials not rings
) but is too close to the line (e.g. if both washer/dryer and dishwasher are on - very likely - they could draw just on 20a, add a kettle to that and it would trip), so to keep it at 32a rcbo, does it sound sensible to use 6mm? The circuit runs in stud will and then in surface boxes and mostly in conduit (since they are behind kitchen units). I am using radials for all my circuits (4mm in other cases), I guess the other option is to put this on a 2.5mm ring at 32a, but this would just double the physical cable sizes. One other issue is that the MK sockets say they can only take 2x 6mm STRANDED, will they actually fit solid core, but just make it harder for me
. I'm not wiring the circuit yet, just planning. Thanks!