yeah I know, sorry lads this one again!
Used the search (as long as I could anyway) re shower cable.
CU s about to be changed along with other configurations, relating to new house extension, having read all previous posts regarding shower cable was eventually able to convince the old fella (retired sparks) that my existing 6mm
suppling a 9.5kw shower needed upgrading to 10mm (6mtr run under floor).
Thought everything was ok until I found out the last 2 feet of cable to the shower is buried behind an uninsulated stud wall which is tiled, part of the shower cubicle passes over the tiles in question, from the limited access I can see the cables have been plastered in as well! I aint gonna get that out without demolishing the whole shower room.
The shower room backs onto the airing cupboard from which the services to the shower are supplied, in here is located the shower switch, It would,nt be a problem for me to get 10mm to this switch, leaving me with about a metre of 6mm to the shower, considering whats been said about 6mm and its performance over distance and other routing factors would this be considered a viable/safe option.
thanks once again
Used the search (as long as I could anyway) re shower cable.
CU s about to be changed along with other configurations, relating to new house extension, having read all previous posts regarding shower cable was eventually able to convince the old fella (retired sparks) that my existing 6mm
suppling a 9.5kw shower needed upgrading to 10mm (6mtr run under floor).
Thought everything was ok until I found out the last 2 feet of cable to the shower is buried behind an uninsulated stud wall which is tiled, part of the shower cubicle passes over the tiles in question, from the limited access I can see the cables have been plastered in as well! I aint gonna get that out without demolishing the whole shower room.
The shower room backs onto the airing cupboard from which the services to the shower are supplied, in here is located the shower switch, It would,nt be a problem for me to get 10mm to this switch, leaving me with about a metre of 6mm to the shower, considering whats been said about 6mm and its performance over distance and other routing factors would this be considered a viable/safe option.
thanks once again