Few reasons for differences, note the CCC always depends on the installation method.
SWA is a different construction to T&E
XPLE SWA is a 90 deg C cable hence it can take more current and run warmer, on the provision that it's terminations are rated to 90 deg C too.
PVC T&E is a 70 deg C cable.
 
Few reasons for differences, note the CCC always depends on the installation method.
SWA is a different construction to T&E
XPLE SWA is a 90 deg C cable hence it can take more current and run warmer, on the provision that it's terminations are rated to 90 deg C too.
PVC T&E is a 70 deg C cable.

PVC SWA is also 70 deg C.
I assume this is what he was comparing against T&E?

Clipped direct, T&E carries 47A compared to PVC SWA carrying 49A.
 
Yep, I imagine it is down to the rate that the cable can dissipate heat as you say.
 