Now we can't figure this out, a few of us at work and those affected (an electrician & an electrical engineer).
Late yesterday a colleague was called to a case of high volts with 800V AC being measured at a customer's premises (an ex-job centre now taken over by a safety advice firm that works at Sellafield.) Coupled with a lost neutral
When our standby crew arrived the electrician told them what he had found and added "you think I'm mad don't you?"
So checks were carried out.
At the single phase (Y or L2) meter position was a cut-out, a mechanical meter, a pair of Henley blocks and 3 CUs all switched off and all MCB.s in the off position
2 of the CUs had double pole main switches, the other only a single pole switch (odd I know but true)
Voltage when measured at the blocks was zero L-N and in the normal range L-E
When one of the double pole CUs was switched on, the L-N voltage leaped from 0 to over 500V and then quickly climbed to 800V, with the (mechanical not the test) meter making a very odd sound!!
Further investigation showed that the neutral was open circuit on the incoming supply cable.
Earthing was TN-S
The electrician also added that whilst investigating and checking the internal wiring he found that at one socket that had been reported as faulty, the neutral and earth were both in the earth terminal.
Obviously this "connection" had been carrying all the load current back to our system since the neutral had been lost on the service cable.
Checking on customers past this point showed there was nothing abnormal with their supplies, so the fault was definitely on the service cable
An excavation showed that the service cable had been damaged, ultimately causing the open circuit neutral, at some time in the past (we don't know when) by BT when a duct had been installed.
The cable was disconnected and terminated, a new piece of service cable joint made to the main and the two service cables jointed together to restore supply. (the damaged service cable did not have enough length on it to make a straight joint but just enough to terminate it).
Now we can fully understand the effects of the lost neutral, the effect of the neutral earth connection in the socket.
We could also understand voltage in the 400V range for a lost neutral on the main (very, very rare on a PILSTA cable), or even a faulty joint where the neutral was open-circuit and then had come in contact with another phase
But where did the measured and witnessed by about 5 folk (our engineer & jointing team, the electrician and the electrical engineer employed by the customer) 800V come from as we have absolutely no idea?
Once the supply was restored to normal at about 02:30 this morning BTW all was fine with no issues.
Late yesterday a colleague was called to a case of high volts with 800V AC being measured at a customer's premises (an ex-job centre now taken over by a safety advice firm that works at Sellafield.) Coupled with a lost neutral
When our standby crew arrived the electrician told them what he had found and added "you think I'm mad don't you?"
So checks were carried out.
At the single phase (Y or L2) meter position was a cut-out, a mechanical meter, a pair of Henley blocks and 3 CUs all switched off and all MCB.s in the off position
2 of the CUs had double pole main switches, the other only a single pole switch (odd I know but true)
Voltage when measured at the blocks was zero L-N and in the normal range L-E
When one of the double pole CUs was switched on, the L-N voltage leaped from 0 to over 500V and then quickly climbed to 800V, with the (mechanical not the test) meter making a very odd sound!!
Further investigation showed that the neutral was open circuit on the incoming supply cable.
Earthing was TN-S
The electrician also added that whilst investigating and checking the internal wiring he found that at one socket that had been reported as faulty, the neutral and earth were both in the earth terminal.
Obviously this "connection" had been carrying all the load current back to our system since the neutral had been lost on the service cable.
Checking on customers past this point showed there was nothing abnormal with their supplies, so the fault was definitely on the service cable
An excavation showed that the service cable had been damaged, ultimately causing the open circuit neutral, at some time in the past (we don't know when) by BT when a duct had been installed.
The cable was disconnected and terminated, a new piece of service cable joint made to the main and the two service cables jointed together to restore supply. (the damaged service cable did not have enough length on it to make a straight joint but just enough to terminate it).
Now we can fully understand the effects of the lost neutral, the effect of the neutral earth connection in the socket.
We could also understand voltage in the 400V range for a lost neutral on the main (very, very rare on a PILSTA cable), or even a faulty joint where the neutral was open-circuit and then had come in contact with another phase
But where did the measured and witnessed by about 5 folk (our engineer & jointing team, the electrician and the electrical engineer employed by the customer) 800V come from as we have absolutely no idea?
Once the supply was restored to normal at about 02:30 this morning BTW all was fine with no issues.