I was helping my in-laws with an issue with one of their ring circuits. AS son as they switch the breaker on at the CU, it trips again. We only have 4 sockets on this ring and nothing was plugged into any of them. I unscrewed each of them and noticed the following:
- the earth wires (unsleeved) were burnt in two of the sockets (possibly next to each other in the ring sequence)
- all of them apart from one socket had power down both ends of the line wire. All others, only had power down one leg of the line
- I have continuity across Neutral and Earth but not Live.
- With one of the sockets, as soon as both Line wires go into the socket or even a wago connector (connecting the two together), it causes the circuit to trip.
I have temporarily resolved this by only connecting one of the live wires to this socket and terminated the other into a wago connector.
I know this will mean that we only have power down one leg of the ring.
Any suggestions on what may be causing this please? I am puzzled by why it only trips when connected to the other leg of Live and not when it is separated from it.
Look forward to your suggestions.
- the earth wires (unsleeved) were burnt in two of the sockets (possibly next to each other in the ring sequence)
- all of them apart from one socket had power down both ends of the line wire. All others, only had power down one leg of the line
- I have continuity across Neutral and Earth but not Live.
- With one of the sockets, as soon as both Line wires go into the socket or even a wago connector (connecting the two together), it causes the circuit to trip.
I have temporarily resolved this by only connecting one of the live wires to this socket and terminated the other into a wago connector.
I know this will mean that we only have power down one leg of the ring.
Any suggestions on what may be causing this please? I am puzzled by why it only trips when connected to the other leg of Live and not when it is separated from it.
Look forward to your suggestions.