Howdy Doody
Sister has an ideal classic boiler with acl lifestyle controls (room stat, digi programmer and the above mentioned valve.
Called round to no radiator heat and found hot water works fine and so does the heating when hot water is called for. Turn off demand for hot water and boiler shuts down even though heat is being demanded.
After a bit of circuit testing and some reading its looking like this valve lifestyle 679h340-30l0.
I moved the manual lever and when turning on boiler heat side fired up.
Shut it down while i relaced programmer cover etc and when back together heat doesnt work anymore.
Had another play with valve manual operating lever and i accidently pushed it in which i believe is supposed to happen to lock it in position.
Instructions state this will release when power is applied to valve but ii doesnt when boiler is fired up. IKts locked in position.
I would like to prove its this valve before i buy a new one (pretty sure after reading a bit it is).
Is there a way i can re-set it so i can move it about again.
Ok with electrics and stripping stuff down.
Currently heating works as long as there is demand for hot water.
Cheers
Sister has an ideal classic boiler with acl lifestyle controls (room stat, digi programmer and the above mentioned valve.
Called round to no radiator heat and found hot water works fine and so does the heating when hot water is called for. Turn off demand for hot water and boiler shuts down even though heat is being demanded.
After a bit of circuit testing and some reading its looking like this valve lifestyle 679h340-30l0.
I moved the manual lever and when turning on boiler heat side fired up.
Shut it down while i relaced programmer cover etc and when back together heat doesnt work anymore.
Had another play with valve manual operating lever and i accidently pushed it in which i believe is supposed to happen to lock it in position.
Instructions state this will release when power is applied to valve but ii doesnt when boiler is fired up. IKts locked in position.
I would like to prove its this valve before i buy a new one (pretty sure after reading a bit it is).
Is there a way i can re-set it so i can move it about again.
Ok with electrics and stripping stuff down.
Currently heating works as long as there is demand for hot water.
Cheers