I'm soon going to be fitting goal post steelword to the rear of our house, whilst I've fitted steel beams before it's never been to this scale, except when I helped the builders over 10 years ago take out the wall in our kitchen which was of similar size.
The opening is going to be 3500mm wide, but due to the columns requiring bolting to the foundations the actual brickwork removed will be wider at foundation level, which is 750mm below DPC.
I plan on using 5 pairs of acrows, spaced at about 810mm centres along the opening, using 47 x 125 x 1200 C16 timbers in pairs as the needles. The outer acrows would be 300mm away from the building, with the inner acrows 400mm away from the wall. Acrows will be screwed to the sole plates and head plate, and needles.
The internal floor is concrete, externally I need to dig down 750mm to the foundation, so the soil at this depth should be pretty well compacted, but sole boards will be used inside and out.
The house is a two storey house with gable end above, 60mm cavity, total wall thickness 265mm, built in the 70's.
Would the above be sufficient to hold the house up whilst the wall is removed to allow fitment of the steelwork?
Would the side return wall require any bracing?
I presume it would be better to install the crossbeam and hold it in place with a couple of acrows. Then remove remove enough wall to hang the columns from the beam, drill the base plate fixing into the foundation and install the studs, then grout under the columns, and once set tighten the nuts?
Edit: Beam will be placed by the wall internally prior to putting the acrows in - best I not forget or it could get rather difficult!
The opening is going to be 3500mm wide, but due to the columns requiring bolting to the foundations the actual brickwork removed will be wider at foundation level, which is 750mm below DPC.
I plan on using 5 pairs of acrows, spaced at about 810mm centres along the opening, using 47 x 125 x 1200 C16 timbers in pairs as the needles. The outer acrows would be 300mm away from the building, with the inner acrows 400mm away from the wall. Acrows will be screwed to the sole plates and head plate, and needles.
The internal floor is concrete, externally I need to dig down 750mm to the foundation, so the soil at this depth should be pretty well compacted, but sole boards will be used inside and out.
The house is a two storey house with gable end above, 60mm cavity, total wall thickness 265mm, built in the 70's.
Would the above be sufficient to hold the house up whilst the wall is removed to allow fitment of the steelwork?
Would the side return wall require any bracing?
I presume it would be better to install the crossbeam and hold it in place with a couple of acrows. Then remove remove enough wall to hang the columns from the beam, drill the base plate fixing into the foundation and install the studs, then grout under the columns, and once set tighten the nuts?
Edit: Beam will be placed by the wall internally prior to putting the acrows in - best I not forget or it could get rather difficult!