Hi all, I have my ACS exams in a few weeks and having a mental block in a home study course, concerning compartment ventilation.
If an open flued 10kw net boiler has compartment ventilation direct to outside, it requires high and low ventilation as follows:
High ventilation is = 5 x 10 = 50cm2
Low ventilation = 10 x 20 = 100cm2
Why is it, if a gas fire (open flue) is fitted within a room you deduct the -7kw for advantageous ventilation.
so: 10 - 7 = 3kw x 5 = 15cm2 ventilation required.
My confusion is, if you -7 Kw for a fire, why is -7kw not deducted from external compartment ventilation for an open flued boiler?
I'm assuming the top external ventilation is for cooling and the bottom ventilation is for combustions so should be worked out same as a gas fire as follows:
Low ventilation: 10kw -7kw = 3 x 5 = 15cm2?
It might seem a stupid question to ask but I'm trying to learn a lot in a short space of time and having a mental block and stopping further progress.
Thanks in advance
If an open flued 10kw net boiler has compartment ventilation direct to outside, it requires high and low ventilation as follows:
High ventilation is = 5 x 10 = 50cm2
Low ventilation = 10 x 20 = 100cm2
Why is it, if a gas fire (open flue) is fitted within a room you deduct the -7kw for advantageous ventilation.
so: 10 - 7 = 3kw x 5 = 15cm2 ventilation required.
My confusion is, if you -7 Kw for a fire, why is -7kw not deducted from external compartment ventilation for an open flued boiler?
I'm assuming the top external ventilation is for cooling and the bottom ventilation is for combustions so should be worked out same as a gas fire as follows:
Low ventilation: 10kw -7kw = 3 x 5 = 15cm2?
It might seem a stupid question to ask but I'm trying to learn a lot in a short space of time and having a mental block and stopping further progress.
Thanks in advance