Please don't shout at me!! I have done quite a bit of research, but am coming up a little short somewhere! So I'll start at the beginning (it seems a good place to start!)....
I bought my house almost 1 year ago exactly, it's my first house. It's a 1990's Bloor Home. One of the first jobs I had to do was sort a shower out. The previous owner had never had a shower on the wall!
So keeping it cheap (I'm going to refit the bathroom soon), I bought a Plumbsure mixer, with showerhead attachment, from B&Q - See here;
http://www.diy.com/diy/jsp/bq/nav.j...mpid=4&tmad=c&ecamp=cse_go&CAWELAID=563954617
Upon installing, I had issues with the hot water pressure. The shower has hot water fed from the gravity hot water system, and the cold from the mains. I have confirmed this as there are only two tanks in the loft - one small overflow for the CH, and one large for the hot water cylinder). Basically the issue was that you can turn the hot water on full, and then just tweak the cold on and the shower runs cold.
Due to the initial poor performance, and after speaking to a couple of plumbing folk, I figured that the issue was unequal pressures. To help solve this, I fitted a isolating valve to the cold water pipe before the tap, and tweaked it until I could mix the shower properly.
The problem with this is that when my girlfriend wants a bath, I have to reopen the isolating valve to get enough cold water. A right PITA as I am sure you can imagine.
So, here is what I have tried/checked;
All valves open
Ball cock floating properly and tank water at a good level
Checked for obstructions in the exit pipe from the header tank
Taps are suitable for low pressure and not 1/4 turn jobies
Tried filling the loft tank more
The reason I'm asking now is because the boiler is on it's last legs. This means I have the age old decision of replacing like for like, or going for a combi. I think a combi would probably help with the flow mismatch, but as the house is a 3 bed detached, so suited for a small family, I believe that stored hot water would be a better option.
This would mean that I still need to improve the shower somehow. I know I can pump it, but I just wanted to check opinions on here first. Am I missing something?
A few system specs;
Boiler: Glow-worm Economy Plus 50F
Water tank height above the shower head: 600mm (give or take 20mm)
Shower head height above the tap outlet: 1450mm
A few pics;
Tap entry to the bath
Hot water cylinder (obviously)
Loft tank - the water sits about 1 inch up the overflow pipe.
Today I have recorded the following flowrates;
From the tap;
Hotwater: 9.1 l/min
Cold restricted: 1.8 l/min
Cold normal: 20 l/min
At the showerhead;
Hotwater: 2.2 l/min
Cold restricted: 1.8 l/min
Cold normal: 10 l/min
Is the flow rate for the hot poor, or the cold flow rate excessive? Have I missed anything? I hope the numbers etc help, I'm an engineer so I love a little bit of data!
Many thanks in advance.
Ian
I bought my house almost 1 year ago exactly, it's my first house. It's a 1990's Bloor Home. One of the first jobs I had to do was sort a shower out. The previous owner had never had a shower on the wall!
So keeping it cheap (I'm going to refit the bathroom soon), I bought a Plumbsure mixer, with showerhead attachment, from B&Q - See here;
http://www.diy.com/diy/jsp/bq/nav.j...mpid=4&tmad=c&ecamp=cse_go&CAWELAID=563954617
Upon installing, I had issues with the hot water pressure. The shower has hot water fed from the gravity hot water system, and the cold from the mains. I have confirmed this as there are only two tanks in the loft - one small overflow for the CH, and one large for the hot water cylinder). Basically the issue was that you can turn the hot water on full, and then just tweak the cold on and the shower runs cold.
Due to the initial poor performance, and after speaking to a couple of plumbing folk, I figured that the issue was unequal pressures. To help solve this, I fitted a isolating valve to the cold water pipe before the tap, and tweaked it until I could mix the shower properly.
The problem with this is that when my girlfriend wants a bath, I have to reopen the isolating valve to get enough cold water. A right PITA as I am sure you can imagine.
So, here is what I have tried/checked;
All valves open
Ball cock floating properly and tank water at a good level
Checked for obstructions in the exit pipe from the header tank
Taps are suitable for low pressure and not 1/4 turn jobies
Tried filling the loft tank more
The reason I'm asking now is because the boiler is on it's last legs. This means I have the age old decision of replacing like for like, or going for a combi. I think a combi would probably help with the flow mismatch, but as the house is a 3 bed detached, so suited for a small family, I believe that stored hot water would be a better option.
This would mean that I still need to improve the shower somehow. I know I can pump it, but I just wanted to check opinions on here first. Am I missing something?
A few system specs;
Boiler: Glow-worm Economy Plus 50F
Water tank height above the shower head: 600mm (give or take 20mm)
Shower head height above the tap outlet: 1450mm
A few pics;
Tap entry to the bath
Hot water cylinder (obviously)
Loft tank - the water sits about 1 inch up the overflow pipe.
Today I have recorded the following flowrates;
From the tap;
Hotwater: 9.1 l/min
Cold restricted: 1.8 l/min
Cold normal: 20 l/min
At the showerhead;
Hotwater: 2.2 l/min
Cold restricted: 1.8 l/min
Cold normal: 10 l/min
Is the flow rate for the hot poor, or the cold flow rate excessive? Have I missed anything? I hope the numbers etc help, I'm an engineer so I love a little bit of data!
Many thanks in advance.
Ian