Dear All
I have a worcester bosh 30CDI conventional boiler fitted into an open vented system. I have a "S" plan design which has the correct dose of Sentinel X100 in it.
I have found that if I set the boiler temperature control to above setting 5, that the system is noisy and constantly requires bleeding at the radiators. It is particulary noisy after the system has been off for over 24hrs. A glugging noise will come up through the motorised valve which controls the feed to the central heating pipes.
I have fitted manual air vents to the system at the highest points and have bled the system from these valves and radiators daily for the past 6 weeks. The system runs smoothly and quietly for a couple of days and then needs to be re-bled
The pipes are all free from blockages and I have a combined feed and expansion pipe. I have done the test at the cistern, with a glass of water and found that the system is not drawing air in through the expansion pipe. Due to the layout in my building the cistern is only about 50cm above the boiler, which does conform to the min height as published in the manual.
I know the simple answer is to not set the boiler temperature control above 5, however I just like to ask the experts who visit this site if they have any ideas which I could i try.
Many Thanks
Bob
I have a worcester bosh 30CDI conventional boiler fitted into an open vented system. I have a "S" plan design which has the correct dose of Sentinel X100 in it.
I have found that if I set the boiler temperature control to above setting 5, that the system is noisy and constantly requires bleeding at the radiators. It is particulary noisy after the system has been off for over 24hrs. A glugging noise will come up through the motorised valve which controls the feed to the central heating pipes.
I have fitted manual air vents to the system at the highest points and have bled the system from these valves and radiators daily for the past 6 weeks. The system runs smoothly and quietly for a couple of days and then needs to be re-bled
The pipes are all free from blockages and I have a combined feed and expansion pipe. I have done the test at the cistern, with a glass of water and found that the system is not drawing air in through the expansion pipe. Due to the layout in my building the cistern is only about 50cm above the boiler, which does conform to the min height as published in the manual.
I know the simple answer is to not set the boiler temperature control above 5, however I just like to ask the experts who visit this site if they have any ideas which I could i try.
Many Thanks
Bob