Alpha 240 combi bolier

Joined
7 Oct 2006
Messages
1
Reaction score
0
Location
Fife
Country
United Kingdom
Hi,

Our boiler is the Alpha 240 combi. When we turn on the hot water it heats up just fine however its strictly one tap at a time. You cant turn on the shower and the kitchen tap at the same time. Any ideas?

Also, only about half of our radiators work. A mix of upstairs and downstairs ones. I have tried bleeding and its a temporarly fix. Next day its back to the same deal.

Whilst i am not particuarly diy savvy i am loathe to call someone out without trying to fix it myself.

Thanks in advance for your help!
 
Sponsored Links
Thats normal for a combi boiler.

Yours only gives about 8 litres per minute of hot water and its up to you to decide which tap(s) to use that from.

Tony
 
You're implying that your rads need frequent bleeding - they shouldn't. It's likely to be corrosion gas collecting in them. That needs attention.
Corrosion blocks radiators too. Try Balancing the rads - see FAQ.

Corrosion products will also reduce the amount of Hot tap water available.
Test the flow at the shower at showering temperature. That should be about 8-10 litres/ minute, depending on the mains temperature. If it's below about 7, it could be improved.
 