Well its been a long day. Couple of services and repairs this morn then started an install this pm. On way home was asked to look at an Alpha CB28.
Not a boiler i am overly familiar with but went along. Both neons lit and for some strange reason the customer was draining a large saucepan of water from the downstairs radiator He thought the flashing neon meant he had to bleed air from the rad. Must have been 1-2 pints in the saucepan Anyway i repressurised, reset and tried to fire it up. Heard the fan, ignition proved with good spark but the main burner would not light. Boiler went into lockout.
Gas is there. checked fan with meter, and cleaned venturi, aps checked and ok, gas valve has 240v on PCB. Was late but am i missing something??
PS: Aahhh?? Does the pump have to be spinning on tjis model to also complete the sequence. Think i missed checking it
Not a boiler i am overly familiar with but went along. Both neons lit and for some strange reason the customer was draining a large saucepan of water from the downstairs radiator He thought the flashing neon meant he had to bleed air from the rad. Must have been 1-2 pints in the saucepan Anyway i repressurised, reset and tried to fire it up. Heard the fan, ignition proved with good spark but the main burner would not light. Boiler went into lockout.
Gas is there. checked fan with meter, and cleaned venturi, aps checked and ok, gas valve has 240v on PCB. Was late but am i missing something??
PS: Aahhh?? Does the pump have to be spinning on tjis model to also complete the sequence. Think i missed checking it