Sorry for the long post, but hopefully I've given all the pertinent facts.
I've got an Alpha CD24S boiler that was installed into an existing CH system in July 2004 along with a new hot water cylinder. The boiler has been serviced annually (last time Oct 2012).
After about 2 years of use, it failed to start one morning because the pressure had dropped too far ( there is a a very small weep from the tank). I topped it up to 1 bar and everything was alright. Since then, we've kept an eye of the pressure and had to top it up once or twice a year.
However, it's now failed three times in 6 weeks. This morning it was topped up to 1 bar (cold), but is now running at 3.6 bar (manufacturers data is max working pressure 2.5 bar).
Is this a failed expansion tank? If it is, Alpha state it is not possible to replace in situ (there is less than 45cm gap above the boiler). Therefore is it possible / acceptable to install an external vessel near the boiler, teed in to the heating return just before the boiler? Does the internal vessel have to be disconnected or just left in situ?
Another thing that concerns me is that the PRV is supposed to be set at 3.0 bar so how is it running at 3.6 bar (faulty gauge?); I cannot see any fluid in the overflow (but it is 15 feet up and it's dark outside). Does this mean the PRV is shot also? If so, can this be replaced DIY as it is not part of the gas system (there is actually a video on YouTube showing how to do it! http://www.youtube.com/watch?v=mQ-tT2PuXdU)
Mike
I've got an Alpha CD24S boiler that was installed into an existing CH system in July 2004 along with a new hot water cylinder. The boiler has been serviced annually (last time Oct 2012).
After about 2 years of use, it failed to start one morning because the pressure had dropped too far ( there is a a very small weep from the tank). I topped it up to 1 bar and everything was alright. Since then, we've kept an eye of the pressure and had to top it up once or twice a year.
However, it's now failed three times in 6 weeks. This morning it was topped up to 1 bar (cold), but is now running at 3.6 bar (manufacturers data is max working pressure 2.5 bar).
Is this a failed expansion tank? If it is, Alpha state it is not possible to replace in situ (there is less than 45cm gap above the boiler). Therefore is it possible / acceptable to install an external vessel near the boiler, teed in to the heating return just before the boiler? Does the internal vessel have to be disconnected or just left in situ?
Another thing that concerns me is that the PRV is supposed to be set at 3.0 bar so how is it running at 3.6 bar (faulty gauge?); I cannot see any fluid in the overflow (but it is 15 feet up and it's dark outside). Does this mean the PRV is shot also? If so, can this be replaced DIY as it is not part of the gas system (there is actually a video on YouTube showing how to do it! http://www.youtube.com/watch?v=mQ-tT2PuXdU)
Mike