Ancient Honeywell Room Stat

Jim

Joined
8 Feb 2003
Messages
164
Reaction score
1
Country
United Kingdom
It is brown with a grey cover plate. Two wires -red to Terminal 1 Neutral to Terminal 3. Earth wire cut back. I get a reading of 12v.
I have found 4 sets of numbers 4200.3879.001(cover Plate)
4200 3840-00(On wallplate)
and inside the stat 42003878.
No joy in establishing replacement spare from suppliers and Honeywell very busy.
The thermostat is not functioning properly. Any advice please on a simple product replacement.
Thanks
Jim
 
Sponsored Links
I imagine you could replace this with the Honeywell DT200
 
Sponsored Links
It is brown with a grey cover plate. Two wires -red to Terminal 1 Neutral to Terminal 3. Earth wire cut back. I get a reading of 12v
It's a Honeywell T6160B!

The blue is NOT a neutral, it's the switched live.

If you use the DT200 suggested, the wiring is:

Red to Terminal A (power from the time switch)
Blue to Terminal B (power to boiler etc)
Earth not required

The blue wire should really have some red sleeving or insulating tape wrapped round both ends to show it is a switched live.
 