I am confused by the different things I read. I have very shallow joists and a low ceiling height. I need to replace ceiling and for Building Control reasons "now" need to get close to the U-Value of 0.18. I can do this, without dropping the ceiling much further by using Actis Triso but they say I need a 50mm void between the deck and the Actis for ventilation (not sure who exactly is insisting on this - Actis or BC). This seems only possible if I put 2 roof vents between each pair of joists. My flat roof will look like a hedgehog and seems eminently likely to increase the chance of leaks!
If I completely tape all edges of the Actis Triso and seal any voids under it, perhaps even adding a further vapour barrier, can I forget about the ventilation? By the way, the original single plasterboard ceiling had no insulation or vapour barrier!
Please help!!!