Ariston Micro Genus 24 Boiler

Joined
11 Oct 2010
Messages
2
Reaction score
0
Location
West Midlands
Country
United Kingdom
Please can you help boiler is about 4 years old had constant problems with fault code E34. Recently had flue and fan checked out ok. Had new air pressure switch fitted. New complete electrical loom fitted. New PCB fitted and fault still wont go. All the engineers are at a loss. PLEASE CAN ANY ONE HELP me. Many thanks
 
Sponsored Links
Did any of them bother to measure the differential pressure across the APS?

On a standard flue the pressure is marginal when they come out of the factory...providing the fan and heat exchanger(s) are clean and the fan is running correctly then removal of the restrictor ring normally resolves an E34. It's a well known fault by now.
 