Hi all, just after a little advice on a DHW flow sensor problem I'm having.
I've noticed recently that the kitchen hot tap needs to be turned to approx half of full flow before the boiler ignites and heats the water. I'm certain it used to turn on at a lower flow rate. Additionally, we recently replaced the shower head with a snazzy one that has micro-jets and which uses less water. The shower now keeps going cold which I can see is because it is using less water, the hot flow rate gets below the threshold and the boiler turns off.
This all points me to the flow rate sensor. I have tried the easy fix and changed the electrical switch as it simply clips onto the HDW inlet by the secondary heat exchanger. However, this hasn't improved the situation at all.
So I now turn to the mechanical part of the sensor - I gather from the internet that this is a part that commonly fails on the Microgenus range. I have ordered and have received a replacement part (this one).
I was going to replace it this weekend as it looked like a simple job. I thought I could turn off the hot/cold water and drain the DHW part of the system, leaving the boiler heating and heat exchanger loop untouched (other than being switched off). The top of the cartridge looks like it would fit an 18mm socket so I thought it would be simple to unscrew and replace with the new one. Unfortunately it appears to be slightly smaller than 18mm but too big for 17mm as the 18mm socket slips as I apply pressure therefore I'll therefore have to remove it with a spanner. The limited room means I'll have to remove the pump and auto air vent so will have to remove the side panel and also therefore remove the cupboard which is boxing in the boiler - this makes it a somewhat larger job!
I just wanted to check therefore that replacing this part is indeed likely to improve the sensitivity of the flow rate sensor?
Thanks in advance - couple of pics below...
I've noticed recently that the kitchen hot tap needs to be turned to approx half of full flow before the boiler ignites and heats the water. I'm certain it used to turn on at a lower flow rate. Additionally, we recently replaced the shower head with a snazzy one that has micro-jets and which uses less water. The shower now keeps going cold which I can see is because it is using less water, the hot flow rate gets below the threshold and the boiler turns off.
This all points me to the flow rate sensor. I have tried the easy fix and changed the electrical switch as it simply clips onto the HDW inlet by the secondary heat exchanger. However, this hasn't improved the situation at all.
So I now turn to the mechanical part of the sensor - I gather from the internet that this is a part that commonly fails on the Microgenus range. I have ordered and have received a replacement part (this one).
I was going to replace it this weekend as it looked like a simple job. I thought I could turn off the hot/cold water and drain the DHW part of the system, leaving the boiler heating and heat exchanger loop untouched (other than being switched off). The top of the cartridge looks like it would fit an 18mm socket so I thought it would be simple to unscrew and replace with the new one. Unfortunately it appears to be slightly smaller than 18mm but too big for 17mm as the 18mm socket slips as I apply pressure therefore I'll therefore have to remove it with a spanner. The limited room means I'll have to remove the pump and auto air vent so will have to remove the side panel and also therefore remove the cupboard which is boxing in the boiler - this makes it a somewhat larger job!
I just wanted to check therefore that replacing this part is indeed likely to improve the sensitivity of the flow rate sensor?
Thanks in advance - couple of pics below...