I seem to be getting a lot of backfeed with CH and HW turned off. 132v on white and orange on 3 port valve.

When CH is on demand I also get 240v on HW on cable to cylinder stat but HW is not turned on at programmer. Is this normal?
 
Sponsored Links
I seem to be getting a lot of backfeed with CH and HW turned off. 132v on white and orange on 3 port valve.
Here's a typical schematic of a 3 port valve in its resting position.

1731840884409.gif

And heres a Y plan layout...

1731841259523.gif


With no call for heat from C/H, or H/W, there should be no feed to either the orange, or white wires from the programmer.
There would be 230V on the grey wire, but given the resting position of the valve, there should be no "backfeed" to any other part of the circuit.
The voltage you are measuring (probably with a high impedance digital multimeter?) may be spurious, caused by cable capacitance, or wiring internal to the boiler.
If you disconnect the Switched Live wire to the boiler, does the voltage dissappear?

When CH is on demand I also get 240v on HW on cable to cylinder stat but HW is not turned on at programmer. Is this normal?
Yes, normal, with C/H only in operation...

1731840501405.gif


Plenty of reading for you here...
 
Last edited:
Sponsored Links
It appears voltage is going to where it should except then pcb on boiler isn't kicking the pump on.... The brown wire in the green blocking was getting 0v. After testing it again it jumped to life.
 

Attachments

  • IMG_20241117_120415.jpg
    IMG_20241117_120415.jpg
    222.2 KB · Views: 7

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top