Indeed - that's exactly what I wrote.On the N-E connection question, that came from here: ... Relevant extract below (my emphasis).
"Most buildings now have an RCD built into the consumer unit. This is configured to operate from the mains supply with an earthed neutral, and not from a generator with a floating earth. To utilize this protection device, it is necessary to modify the generator so that it is configured in the same way as the mains supply.
As I (and also Simon) said, that is neither the usual, nor a desirable, way to earth the neutral side of the genny output. It should really be done within the generator, not in a plug. As I said, it is crucial for you to determine what, if anything, is connected to the 'earth terminals' (e.g. of output socket) within your generator before you even think of connecting N and E (anywhere)..... This is a simple modification for a qualified electrician, involving adding a link wire from the neutral terminal to the earth terminal. It is recommended to make this connection in the plug that is to be used to connect to the generator.
I'm not sure in what sense they are suggesting that a generator would become 'unsafe' if it had an internal N-E link. Generators are (should!) rarely used with 'floating' outputs....This ensures that the generator is unmodified when it is disconnected from the house, and therefore remains safe.
The labelling would certainly reduce the hazard to some extent, but I still would not personally advocate that approach. What they say about the SWA is correct as is (as you know) what they say about an 'earth spike'....The plug should be labeled “Do not connect to mains: Neutral-Earth link fitted”. The lead between the generator and the transfer switch is not protected by the RCD, it is therefore recommended to use a steel armored cable for this connection. Finally a local low-impedance earth spike needs to be installed.
Probably not, but I would personally say that the advice being given is not very wise What do others think?Have I misunderstood that?
Yes, it probably would, but that could be a pretty small box so that, even together, I imagine that that plus the MSF100 would be a lot smaller than your current switchfuse.Thanks for link to the small fused switch. That would do the job but I suppose would need an intermediate metal box to terminate the SWA.
Kind Regards, John