I woke up last week to the sockets not working in the house, reset the rcd and all was fine......for 2 days.
Then it happened again. This time I traced a burning smell to the airing cupboard. It was coming from the 3 port mid position valve (a drayton 670H340-30L0).
Inside the valve resistor R1 was charred but showing 2K7 on a meter, is this the correct value? What would cause this to happen? (Drayton refuse to tell me the value of this component - awful customer service). It seems that the neutral connection to the valve had never been screwed down and was loose. R2 on the board is OK at 67K.
The valve works and so does the HW and CH, but the RCD still trips occasionally and today would not reset until the boiler power had been removed. Restoring boiler power does not cause an RCD trip!
The synchron motor measures 2K6 across it's windings and infinity from the windings to the case, so not likley to have earth leakage current there.
I disconnected the m/p valve and all is well, but no CH!
Can I temporarily connect a live to where the m/p orange wire connects into the distribution to 'enable' the CH from the boiler?
Can anyone help me with this please?
Andrew
Then it happened again. This time I traced a burning smell to the airing cupboard. It was coming from the 3 port mid position valve (a drayton 670H340-30L0).
Inside the valve resistor R1 was charred but showing 2K7 on a meter, is this the correct value? What would cause this to happen? (Drayton refuse to tell me the value of this component - awful customer service). It seems that the neutral connection to the valve had never been screwed down and was loose. R2 on the board is OK at 67K.
The valve works and so does the HW and CH, but the RCD still trips occasionally and today would not reset until the boiler power had been removed. Restoring boiler power does not cause an RCD trip!
The synchron motor measures 2K6 across it's windings and infinity from the windings to the case, so not likley to have earth leakage current there.
I disconnected the m/p valve and all is well, but no CH!
Can I temporarily connect a live to where the m/p orange wire connects into the distribution to 'enable' the CH from the boiler?
Can anyone help me with this please?
Andrew