Further to other questions i've asked... I'm fitting a whirlpool bath.. yes using RCD etc.. :eek:
but I know that you must have an external switch for a shower (10.8kw), do i need one for the whirlpool? :?: I've been told that the bath draws 3A, 5A at startup. Also with the cable under floorboards what cable size would you use? 2.5mm? or can i use smaller?... i've got loads of 1.5mm cable around. :?:
 
Sponsored Links
Use a DP switched FCU, 5A fuse - that will give you the isolation control that you need and allow you to use 1.5mm² cable on the load side.
 
but do i actually need a fcu?

the bath will be connected to a shower consumer unit RCD protected(with 10A MCB feeding the bath and a 50A connecting to a shower ) which will then be connected to a main consumer unit with a 50A MCB which is in turn protected by a 100A incomer.
surely if i want to isolate it i could trip the RCD, the 10A MCB, the 50A MCB in the consumer unit or even the 100A incomer..or all 4 to be really safe!!!!

i could always drop the 10A MCB to a 6A to protect the cable to the bath.? :confused:
 
No, you need an FCU, think about it. If something goes wrong with that bath, it could draw a lot of current which its circuitry probably isnt designed for, so you need a 5A rated fuse in a FCU. Also, like the shower and your cooker and all other appliances, you want local isolation, and i think this is also a requirement, especially in bathrooms. Just fit a FCU outside the bathroom in the hallway. Really, these things should be turned off when not in use. But then who pulls the cord after they've finished a shower? :rolleyes:
 
Sponsored Links
crafty1289 said:
No, you need an FCU, think about it. If something goes wrong with that bath, it could draw a lot of current which its circuitry probably isnt designed for, so you need a 5A rated fuse in a FCU.
Depends what the makers say - it might be perfectly OK to use a 6A MCB. (BTW, dabaldie, 10A is fine for 1.5mm²).

Also, like the shower and your cooker and all other appliances, you want local isolation, and i think this is also a requirement, especially in bathrooms. Just fit a FCU outside the bathroom in the hallway. Really, these things should be turned off when not in use.
With protection (possibly) elsewhere, a pullcord in the bathroom might be preferable. Who knows.

But then who pulls the cord after they've finished a shower? :rolleyes:
I do, and so do all the others in our house, otherwise the extractor fan runs for ever.... ;)
 
BAS, I guess pulling the shower switch a habit thing, we never got into it. My parents dont either. Our shower even has a red light on it that stays on as long as the power supply is on, its on all the time! :confused:

Do you have the fan wired into the shower switch? I never thought about doing that, how does that work then? FCU and fan isolator on shower circuit i guess? Or did you mean the light switch?

ban_all_sheds said:
a pullcord in the bathroom might be preferable. Who knows.

As long as its not right next to the light switch, the person having a bath may end up in complete darkness! This would also mean running the cable into the roof space, then back down to the bath. More trouble than its worth i think!!!! ;)
 
crafty1289 said:
Do you have the fan wired into the shower switch? I never thought about doing that, how does that work then? FCU and fan isolator on shower circuit i guess? Or did you mean the light switch?
The fan is controlled by the shower switch but supplied by the lighting circuit. I did it that way using a contactor to get round the problems of having to fuse down from 50A to 3A, and get multiple 10mm² cables into the switch.

See all the gory details here: //www.diynot.com/forums/viewtopic.php?p=123601#123601
 