Wow, that's a huge notch out of that joist. Was it existing or have you just made it? Notches should be no more than 12.5% of the total depth of the joist.
As to your question, you'd normally put a 110mm tee in there, with a reducer in the end to take the waste. Having a pan connector under the floor like that isn't a good idea
I'd put one of these into the tee https://www.mrcentralheating.co.uk/110mm-x-50mm-black-solvent-weld-soil-to-waste-reducer then use a reducer to bring to down to the required size. It should actually help to keep the soil pipe cleanHi, Cheers for the response. The notch was already there, your right it is on the large side though!
So would you do it like this (attached pic)? Would I get any effluent pushed back towards the 40mm pipe when the toilet is flushed do you think?
I'd put one of these into the tee https://www.mrcentralheating.co.uk/110mm-x-50mm-black-solvent-weld-soil-to-waste-reducer then use a reducer to bring to down to the required size. It should actually help to keep the soil pipe clean
View attachment 224346
If that main soil pipe gets restricted or blocks for any reason then yes, the minute you pull the handle the waste will travel up into the bath. Or if there is a main stack venting issue then it can pull on the bath trap. IMO that's a problem waiting to happen.Would I get any effluent pushed back towards the 40mm pipe when the toilet is flushed do you think?