Hi all, Its seems that most comments regarding the location of an extractor fan in zone 2 and indeed zone 1 must be selv/12volts. Please correct me if I'm wrong here but my understanding is you can fit a 230volt ex/fan in zone 2 if its ipx4 or above and in zone 1 ipx5 if you cannot fit one in zone 2 or outside of zone 2. Isolator switches, heres another one, I've seen comments that these MUST be mounted outside the bathroom period!! if you mount one inside the bathroom, outside the zones ie above the 2.25 you are fully complying with the regs are you not??? at the end of the day a normal light pull switch is located in the same position is it not? It would be nice if someone made a IPX4 or above isolator switch but I dont know of any. Please let me stress that the above is assuming the installation complies with the 17th ed to start with. If you think I've got this wrong please please let me know, but please just dont say no your wrong, explain way. If I am wrong I think I'll give away my tools and stop testing now. Thanks