Right guys,
Gone round to a boiler fault which at first appeared to be the Diaphram on the above mentioned Boiler however boiler also seemed to be overheating, changed diaphram which indeed was knackered.
Boiler Still Overheating only now instant however central heating works perfect.
Changed Plate Heat Exchanger which was all crapped up but boiler still instantly over heating on DHW.
I have checked the 3 port valve switch (Big Electric Block) which apears to be working fine.
Any Ideas?
Thanks
Chuck