I have a Baxi platinum 28he combi boiler and recently it has been losing its pressure.
I have called out several different engineers now but they have all failed to fix the problem.
I have followed some advice found on this website and from other sources and I believe the problem is now a leak somewhere between the boiler and radiators but I thought I would run this by you just in case something has been missed?
So far - the expansion vessel has been replaced and repressurised. The heat exchanger was replaced. The PRV was replaced.
There is no signs of any leaks within the boiler.
The inlet and outlet valves were shut off and the boiler pressure monitored over 3 hours- there was no pressure lost.
When the valves were turned back on the pressure dropped by about 0.3bar.
The system was then repressurised to 1.5 bar and then the hot tap opened. The pressure drops to about 1.2 bar whilst the hot tap is running. When the hot tap is closed the pressure rises back to 1.5bar.
The heating is then turned on. The pressure drops again to about 1.2 bar immediately before rising up to 1.7 and holds at that.
There are only 3 double radiators in the house and a heated towel rail. I have checked all the valves etc. There are no signs of any leaks anywhere. They all heat up very quickly.
After turning the heating off the pressure stays the same for about 45mins but slowly losses presure over 12 hours.
There is no signs of water from the prv pipe outside.
There was a small drop of water coming from the Magna Clean lid but that was tightened up.
Am I right in thinking that the probable cause of pressure loss is a leak in the pipework between boiler and radiators?
I have called out several different engineers now but they have all failed to fix the problem.
I have followed some advice found on this website and from other sources and I believe the problem is now a leak somewhere between the boiler and radiators but I thought I would run this by you just in case something has been missed?
So far - the expansion vessel has been replaced and repressurised. The heat exchanger was replaced. The PRV was replaced.
There is no signs of any leaks within the boiler.
The inlet and outlet valves were shut off and the boiler pressure monitored over 3 hours- there was no pressure lost.
When the valves were turned back on the pressure dropped by about 0.3bar.
The system was then repressurised to 1.5 bar and then the hot tap opened. The pressure drops to about 1.2 bar whilst the hot tap is running. When the hot tap is closed the pressure rises back to 1.5bar.
The heating is then turned on. The pressure drops again to about 1.2 bar immediately before rising up to 1.7 and holds at that.
There are only 3 double radiators in the house and a heated towel rail. I have checked all the valves etc. There are no signs of any leaks anywhere. They all heat up very quickly.
After turning the heating off the pressure stays the same for about 45mins but slowly losses presure over 12 hours.
There is no signs of water from the prv pipe outside.
There was a small drop of water coming from the Magna Clean lid but that was tightened up.
Am I right in thinking that the probable cause of pressure loss is a leak in the pipework between boiler and radiators?