Baxi 80HE noisy DHW

Joined
27 Jan 2007
Messages
5
Reaction score
0
Location
Essex
Country
United Kingdom
I have a Baxi 80 HE. The problems is as follows. Turn on hot water tap, all ok. When I turn it off I get a loud high pitched noise! I've discovered that when I tap or pull (very gently) on the DHW pressure diff valve the noise disappears, only to return next time. :mad:

Any help/ideas greatly appreciated!
 
Sponsored Links
Yes. Sorry, didn't realise there were different types of 80 HE :confused:
 
Replacing the 'O' rings in the diverters cures this, or simply replace the diverter valves themselves.
 
Sponsored Links
Thanks for that! Do you know of any links to exploded diagrams, etc please?
 
Hi again. Had a look at the website. Doesn't show any O rings.

Are they in the diverter valve itself or in each of the DHW & CH pressure differential valves?

Many Thanks
 
Valves complete
248727 E68184 Valve - 3 Way Assembly x 1
248728 E68185 Pressure Differential Assembly x 1

Sorry, thought the 'O' rings were available seperately but I can't locate a part number.
 
Brilliant. Thank you very much for all your help! I'm surprised I'm having to replace anything really. Boiler's only 18 months old! Perhaps this is quite common though? :rolleyes:
 