Baxi Avanta not showing pressure

Joined
14 Jul 2009
Messages
29
Reaction score
0
Location
London
Country
United Kingdom
Hi all,
My boiler was flashing with an E9 error this morning as is reading 0 bar pressure; but when i topped up using the filling loop the needle didn't move.
Could hear water going in, then can hear not much more really able to go in, so have let a bit out of the boiler so not too high (and repeated a couple of times to check)

Have bled radiators and was no air in system, any ideas what the issue might be?

Thank you.

Kev
 
Sponsored Links
Gauge plastic tube is probably blocked at the boiler connection...new gauge required or blockage cleared out.
 
Thank you, i thought it might be. Will try and get sorted, hopefully it's nothing more sinister further in!
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top