Hi All,
I have a Baxi Back boiler 50/4E Gravity fed hot water paumped CH system with a two port (Honeywell) valve on the hot water return.
Right that's the system, heres the problem.
Timer 1 7am-9am Boiler fires up heating and hot water works fine swithces off at 9am no problems.
Timer 2: 5pm-9pm, Boiler fires up, cylinder reaches temp valve shuts of the gravity return. Heating works fine, noise free and nice an snug. Roomstat appears to work okay. Activtes/deactivates boiler.
Issue is that on timer 2 run after about 2.5-3hrs the radiators get very hot and noise begins to appear, clunking and banging. If I check the pipes they appear to be getting too hot.
Tests and checks done;
Balance seems okay; F-R 10C diff. same as flow return to boiler.
Pump is set on Low, (setting on 2 drops this diff to 7C.)
Flow Temp is 80C Return is 70C (when 'working' okay)
All TRV's have TRV bodies removed so all are fully open.
Pump activates/deactivates on Roomstat reaching temp.
Motorised valave operates on Cylinder reaching temp.
What happens is the boiler appears to start short cycling and overheating even though the roomstat and Cylinderstat are no longer calling for heat.
My logic concludes there is a boiler interlock fault and maybe the connections (for Valve perhaps) aren't switching off the boiler. This would be okay (though not ideal) as the boilerstat would kick in and switch off.
But if the Boilerstat is faulty AND there is an interlock issue then I guess these two together could give the symptoms I'm seeing.
Anyone with greater experience in CH and issues pertaining like to confirm my analysis or suggest other possible reasosn for the fault?
I have a Baxi Back boiler 50/4E Gravity fed hot water paumped CH system with a two port (Honeywell) valve on the hot water return.
Right that's the system, heres the problem.
Timer 1 7am-9am Boiler fires up heating and hot water works fine swithces off at 9am no problems.
Timer 2: 5pm-9pm, Boiler fires up, cylinder reaches temp valve shuts of the gravity return. Heating works fine, noise free and nice an snug. Roomstat appears to work okay. Activtes/deactivates boiler.
Issue is that on timer 2 run after about 2.5-3hrs the radiators get very hot and noise begins to appear, clunking and banging. If I check the pipes they appear to be getting too hot.
Tests and checks done;
Balance seems okay; F-R 10C diff. same as flow return to boiler.
Pump is set on Low, (setting on 2 drops this diff to 7C.)
Flow Temp is 80C Return is 70C (when 'working' okay)
All TRV's have TRV bodies removed so all are fully open.
Pump activates/deactivates on Roomstat reaching temp.
Motorised valave operates on Cylinder reaching temp.
What happens is the boiler appears to start short cycling and overheating even though the roomstat and Cylinderstat are no longer calling for heat.
My logic concludes there is a boiler interlock fault and maybe the connections (for Valve perhaps) aren't switching off the boiler. This would be okay (though not ideal) as the boilerstat would kick in and switch off.
But if the Boilerstat is faulty AND there is an interlock issue then I guess these two together could give the symptoms I'm seeing.
Anyone with greater experience in CH and issues pertaining like to confirm my analysis or suggest other possible reasosn for the fault?