Hi, hoping someone here can help me with some advice? Recently moved to a house that was built in 1999, it has a baxi bahama 100 combi boiler. CH is working but I'm having trouble getting even heating throughout the house. I've noticed that the pressure gauge drops even though I'm regularly setting 1bar using the fill loop - sometimes twice a day (morning and evening).
Tonight I checked the pressure vessel, which looks quite new, it was reading 27.5psig with the boiler hot. I have read that it should be 1 bar / 14.7psig. Should I adjust it by letting some air out? If so, is it o.k. to do that with everything at temperature, or should it be done with the system cold?
Thanks in advance for ant help or advice, this is driving me mad!
Tonight I checked the pressure vessel, which looks quite new, it was reading 27.5psig with the boiler hot. I have read that it should be 1 bar / 14.7psig. Should I adjust it by letting some air out? If so, is it o.k. to do that with everything at temperature, or should it be done with the system cold?