Ok here goes, hot water is working as it should, CH is dead.
Actuator moves when tap turns on, flowswitch is open circuit,shows continuity when tap turns on, water heats, all seems ok.
Move selector to dhw and ch, and the above is still true. Turn off tap and the actuator returns. Roomstat creates demand for heat, timer on constant and nothing happens. To check the CH flowswitch it is open circuit, removed actuator head, turned on tap, pump runs, flowswitch shows continuity. Radiators heat up until of course the tap is turned off.
From this, and the assumption that something must start the pump running before the CH flowswitch can work, am i looking at the pcb?
There are 3 relays on this board and again i assume one of them switches the roomstat signal to the pump.
anybody know which one? or have i missed something else?
(yes i know its a bahama, but in 8years this is the first problem i've had)
Tim
Actuator moves when tap turns on, flowswitch is open circuit,shows continuity when tap turns on, water heats, all seems ok.
Move selector to dhw and ch, and the above is still true. Turn off tap and the actuator returns. Roomstat creates demand for heat, timer on constant and nothing happens. To check the CH flowswitch it is open circuit, removed actuator head, turned on tap, pump runs, flowswitch shows continuity. Radiators heat up until of course the tap is turned off.
From this, and the assumption that something must start the pump running before the CH flowswitch can work, am i looking at the pcb?
There are 3 relays on this board and again i assume one of them switches the roomstat signal to the pump.
anybody know which one? or have i missed something else?
(yes i know its a bahama, but in 8years this is the first problem i've had)
Tim