GC 47 075 16
The heating is non-existant, DHW performance is poor and the pre-heat takes forever. Typical sludged up system.
The main problem however is the return pre-formed pipe connection between the return isolating cock and the lower connection on the pump back casing.
I removed this pipe to gain access to the return filter located in the isolating valve. When I replaced the connection pipe (it also has the pressure gauge tapping) and locked the O ring seal into the pump housing with the screw the lower flange was 8mm short of the isolating valve.
1/2 Hour on the phone to Baxi got no where. They deny this part was sent out too short. In the end I used 3 fibre washers to make up the gap with the O ring just sealing (but not locked in with the screw). This is how it was previously installed by the cowboys 2 years ago. The other odd thing is the PRV pipe from the valve to the wall jig. This has an end feed coupling soldered to extend the lenght - were these also formed too short?
Any Baxi regulars any idea? The boiler is definately fitted to the wall jig correctly (if it wasn't the other connections wouldn't fit properly).
The image shows the pipe packed out with washers, the O ring joint is not fiully pushed home and the boiler pressurised just enough to get hot water.
The heating is non-existant, DHW performance is poor and the pre-heat takes forever. Typical sludged up system.
The main problem however is the return pre-formed pipe connection between the return isolating cock and the lower connection on the pump back casing.
I removed this pipe to gain access to the return filter located in the isolating valve. When I replaced the connection pipe (it also has the pressure gauge tapping) and locked the O ring seal into the pump housing with the screw the lower flange was 8mm short of the isolating valve.
1/2 Hour on the phone to Baxi got no where. They deny this part was sent out too short. In the end I used 3 fibre washers to make up the gap with the O ring just sealing (but not locked in with the screw). This is how it was previously installed by the cowboys 2 years ago. The other odd thing is the PRV pipe from the valve to the wall jig. This has an end feed coupling soldered to extend the lenght - were these also formed too short?
Any Baxi regulars any idea? The boiler is definately fitted to the wall jig correctly (if it wasn't the other connections wouldn't fit properly).
The image shows the pipe packed out with washers, the O ring joint is not fiully pushed home and the boiler pressurised just enough to get hot water.