Baxi Duotec 28 He Combi Boilercode E133 keeps coming on and having to reset over the last 2 months but is taking more resets to reset it reset and at the moment won't reset please help :cry:
 
Sponsored Links
Sponsored Links
only things that can cause E133 are

1) electrode spark gap
2) ignitor unit
3) fan venturi tube kinked
4) gas valve

I find every 12 months the electrode needs the spark gap adjusting
 
Thanks for advice every body, it was electrode gap had closed up 2 minute job for fitter no charge as I know him :) :)
 
Was your boiler firing at all?

Because I'm getting the same error message, but dont see how it could be the spark gap if my boiler fires and runs for a while (1 / 2 minutes) then cuts out and displays error 133?

Any help would be greatly appreciated
 