Hi Darren, sorry to jump on your thread but I have nearly exactly the same problem with exactly the same boiler.
I have so far cleaned out the flow valve, replaced the diaphragm, cleaned the pin and put new silicone Plumba grease on it.
I've also checked the heat exchanger for blockages (was replaced only last year and very clean).
I have an external pressure vessel and the main line to it was clogged. Cleaned that out and flushed it, checked charge in pressure vessel at 2 bar (also replaced last year).
Recharge system to 1-1.5 bar and the proving pin FIRES into life. After running the boiler for a few mins the pin gets weaker and weaker.
Boiler kicks off and on reset the pin does not push out any more (or just a little). Bleed all radiators but still no major movement on the pin.
I've got a mag filter on the return line and have checked that (all clear bar a little bit of buildup).
Reconnected, bled, still nothing.
If I restrict the flow on a main valve the pin comes out.
I'm thinking either a fault flow valve (even though I have checked it over) or a blockage somewhere else in the circuit.
Any ideas would be greatly appreciated.
I have so far cleaned out the flow valve, replaced the diaphragm, cleaned the pin and put new silicone Plumba grease on it.
I've also checked the heat exchanger for blockages (was replaced only last year and very clean).
I have an external pressure vessel and the main line to it was clogged. Cleaned that out and flushed it, checked charge in pressure vessel at 2 bar (also replaced last year).
Recharge system to 1-1.5 bar and the proving pin FIRES into life. After running the boiler for a few mins the pin gets weaker and weaker.
Boiler kicks off and on reset the pin does not push out any more (or just a little). Bleed all radiators but still no major movement on the pin.
I've got a mag filter on the return line and have checked that (all clear bar a little bit of buildup).
Reconnected, bled, still nothing.
If I restrict the flow on a main valve the pin comes out.
I'm thinking either a fault flow valve (even though I have checked it over) or a blockage somewhere else in the circuit.
Any ideas would be greatly appreciated.