This boiler is a heat only system. Started last year not getting the rads anyware near as warm as usual, although it has been fine for several years running at about 5 on the boiler control setting. Fixed a clip on thermometer onto flow pipe from boiler, and only read 60ish Deg. Should be around 80 deg. I believe. Suspected that the control pot (boiler setting) may be faulty, but exchanged that with no change. Replaced clip-on thermister on boiler outlet pipe, no change. Fitted new PCB, no change. I have just tried removing clip-on thermister from outlet pipe temporarily, and temperature did start to rise so I thought I might have a faulty replacement, until at about 65 deg. the overheat device triggered! Cant see them both being faulty, and tried several times with same result. The boiler works fine in all other respects, flame, heat up time, etc. Struggling now, anyone any ideas please? Searched but can't find anyone else with the same problem. Steve